RE: 30 amp service for storage -
Richard - 08-26-2021
Dave,
Your system with two inverters may require both of the hot legs to be powered in order to supply 110 to the necessary circuits. If that is the reasoning then a garden variety 30 amp to 50 conversion plug will work. You will not have 220 volts for stove top, aquahot, or dryer. You probably can run 1 AC. But your batteries, refrig, and electronics will be fine. There are some concerns with the Newell splitter that are too much for me to type on my phone
RE: 30 amp service for storage -
kmeinke - 02-21-2022
Steve
I have a similar situation in our storage building. I also plan on using a y-adapter to plug into two separate circuits
Does your chassis battery charger trip your breaker. According to the Newell operating manual, that chargers draws 21 amps (at full load). I have been hesitant to plug it in
Thanks
Ken
RE: 30 amp service for storage -
Richard - 02-21-2022
Ken,
Most charger/inverters have a an option for you to limit the amount of current it draws, or set it for incoming 50/30/20 amp service