You are not logged in or registered. Please login or register to use the full functionality of this board...
Newell Gurus
Aquahot reading LO on display - Printable Version

+- Newell Gurus (https://newellgurus.com)
+-- Forum: Documentation (https://newellgurus.com/forumdisplay.php?fid=13)
+--- Forum: Plumbing and fixtures (https://newellgurus.com/forumdisplay.php?fid=39)
+--- Thread: Aquahot reading LO on display (/showthread.php?tid=6516)



Aquahot reading LO on display - B and C - 12-23-2021

Good afternoon,

Just returned from storage and noticed the Aquahot was reading LO on the inside display.  It is switched on electric and I am wondering what I should look for when checking?  Only have 30 amp service.

Thanks,
 B and C
2002 Newell #636


RE: Aquahot reading LO on display - bestgenman - 12-23-2021

The big heating element in your AH is 240V.  The 30A shore power is 120V, it may come up to temp if the 120V 1600W element is working and so connected electrically.  Your diesel should bring the temp up if working correctly.


RE: Aquahot reading LO on display - Trainer - 12-24-2021

From ambient to full temp on the 120 vac element is 2 to 3 hours. The diesel burner will heat it up in 15 to 20 minutes max. Once the temp is high enough, the meter will read in degrees.