Have run into strange problem. Have lost both galley oversink 110v receptacles
and bedroom receptacle. Sink ones are through inverter, but bedroom is not.
No power on shore or battery/inverter power. Everything else is fine.
Strange thing is bedroom receptacle is not through inverter and shows power
at breaker. Would have thought galley ones would be gfi., but are not.
Maybe description on breaker box in wrong.
Any thoughts on my problem or has anyone seen something like this?
(12-28-2016, 09:08 PM)encantotom Wrote: Sounds like you have a GFI outlet popped somewhere
Tom
I checked that Tom. The only one I can find is the one in the bathroom and it works okay.
Did Newell ever use stand alone gfi's away from the receptacle, and not on the breaker?
We had similar issues with manufactured home a couple of times. Electrician from factory came out and fixed all 3 times. First time we had lost an outlet and hall light. It turned out to be a bad connection in light junction box. Second time we lost some outlets in different rooms. It turned out to be a bad connection in one outlet junction box. All were fed off same circuit. Last time we lost some outlets in both bathrooms. He looked for quite a while to find that the problem was a popped gfi. It seems that somehow 1 circuit had 2 gfi's on it and only one popped.
Thanks everyone, turns out to be a severe case of operator error. Original problem was tripped gfi
in bathroom. After I reset it, checked all receptacles with my tester pen, and found that 3 did
not register. This morning plugged in a small heater and it worked!
For some reason my non contact voltage detector pen will not read these 3 receptacles.
Next time I will use a real voltmeter.