06-18-2023, 06:18 PM
That's how I sum up my air conditioning repair skills....
I soldered in the condenser coil today and nitrogen pressure tested it. Held without issues for an hour. I vacuumed it down to 370 microns. it held and balanced at a max of 1400 after an hour. charged it with about 30 oz of R22 and temps seem right on. Can you fellow A/C gurus see anything wrong with what I have going on? Reason I ask is that the unit label shows a max charge of 22oz at 24' of line-set. I have about 26-28' and the amperage is holding around 20.1amps with it maxed at what is in the pic. (This is indoor and outdoor consumption) Temps are about 109º out. Discharge air is 44º
I soldered in the condenser coil today and nitrogen pressure tested it. Held without issues for an hour. I vacuumed it down to 370 microns. it held and balanced at a max of 1400 after an hour. charged it with about 30 oz of R22 and temps seem right on. Can you fellow A/C gurus see anything wrong with what I have going on? Reason I ask is that the unit label shows a max charge of 22oz at 24' of line-set. I have about 26-28' and the amperage is holding around 20.1amps with it maxed at what is in the pic. (This is indoor and outdoor consumption) Temps are about 109º out. Discharge air is 44º
--Simon
1993 8v92TA #312