Steve,

Sounds like like your chassis batteries had dead cell(s) and the inverters just continued charging because they could never get to the float voltage. You can use the wet cell charging parameters with Lifeline AGM's the numbers are close enough. Some inverters don't have an AGM setting, that seems to come up all the time.

Tom