You are not logged in or registered. Please login or register to use the full functionality of this board...
Newell Gurus
Mach 15 A/C Fans Intermittent - Fixed - Printable Version

+- Newell Gurus (https://newellgurus.com)
+-- Forum: Technical Discussions (https://newellgurus.com/forumdisplay.php?fid=3)
+--- Forum: Air Conditioning (https://newellgurus.com/forumdisplay.php?fid=8)
+--- Thread: Mach 15 A/C Fans Intermittent - Fixed (/showthread.php?tid=8942)



Mach 15 A/C Fans Intermittent - Fixed - hypoxia - 05-01-2026

Number 1 & 3 rooftop A/C unit fans would start-stop-start-stop-start & run.  Both units started doing that on the same day.  I checked the fan capacitors, they were out of tolerance.  Then I found an intermittent start capacitor and a run capacitor out of tolerance.  I ended up replacing all four A/C units fan (7.5uf) and run (40uf) capacitors and replaced the 4 start capacitors & PTCR's with Supco SPP6 .  Then I cleaned the evaporator coils and condenser coils.  I checked the compressor terminals, they were good, it's not uncommon to find an overheated terminal on the compressor.  I move the terminal back & forth to ensure a good connection.  I spent wo days on that project, hopefully it cured the intermittent fan problem.


RE: Mach 15 A/C Fans Intermittent - Fixed - encantotom - 05-01-2026

hi jim, do you have soft starts on them?

tom


RE: Mach 15 A/C Fans Intermittent - Fixed - hypoxia - 05-01-2026

(05-01-2026, 08:57 AM)encantotom Wrote:  hi jim,  do you have soft starts on them?

tom
No.  Here's a photo of the intermittent capacitor.

   


RE: Mach 15 A/C Fans Intermittent - Fixed - [email protected] - 05-01-2026

I have those SPP6's on all four of my SCS compressors. Helps keep from slamming the generator with a big load when the compressors kick on. I keep a couple spares as well.


RE: Mach 15 A/C Fans Intermittent - Fixed - hypoxia - 06-09-2026

I thought the problem of the A/C fan starting on-off-on-off over & over was cured but it kept doing it.  Turns out the new Silverleaf TM200 with firmware 1.39 that I acquired a few months ago has programming problems.  I installed the original TM200 with firmware 1.16 & the A/C units are working correctly now.  

The folks at Trillium are working on a new firmware to resolve the problem.  The new TM200's have a different processer which requires programming changes & apparently I'm one of the guinea pigs.


RE: Mach 15 A/C Fans Intermittent - Fixed - [email protected] - 06-09-2026

(06-09-2026, 05:09 AM)hypoxia Wrote:  I thought the problem of the A/C fan starting on-off-on-off over & over was cured but it kept doing it.  Turns out the new Silverleaf TM200 with firmware 1.39 that I acquired a few months ago has programming problems.  I installed the original TM200 with firmware 1.16 & the A/C units are working correctly now.  

The folks at Trillium are working on a new firmware to resolve the problem.  The new TM200's have a different processer which requires programming changes & apparently I'm one of the guinea pigs.

Hmm, that module would be taken out from controlling my AC’s, but that’s me. I guess this is the stuff that allows you to control everything from an IPad or HMI interface? I have remote control for my AC’s through my thermostats that I changed, that is good enough for me. Glad you guys are out there figuring this stuff out Jim, this I am sure will help some others at some point.