Mach 15 A/C Fans Intermittent - Fixed - hypoxia - 05-01-2026

Number 1 & 3 rooftop A/C unit fans would start-stop-start-stop-start & run.  Both units started doing that on the same day.  I checked the fan capacitors, they were out of tolerance.  Then I found an intermittent start capacitor and a run capacitor out of tolerance.  I ended up replacing all four A/C units fan (7.5uf) and run (40uf) capacitors and replaced the 4 start capacitors & PTCR's with Supco SPP6 .  Then I cleaned the evaporator coils and condenser coils.  I checked the compressor terminals, they were good, it's not uncommon to find an overheated terminal on the compressor.  I move the terminal back & forth to ensure a good connection.  I spent wo days on that project, hopefully it cured the intermittent fan problem.


RE: Mach 15 A/C Fans Intermittent - Fixed - encantotom - 05-01-2026

hi jim, do you have soft starts on them?

tom


RE: Mach 15 A/C Fans Intermittent - Fixed - hypoxia - 05-01-2026

(05-01-2026, 08:57 AM)encantotom Wrote:  hi jim,  do you have soft starts on them?

tom
No.  Here's a photo of the intermittent capacitor.

   


RE: Mach 15 A/C Fans Intermittent - Fixed - [email protected] - 05-01-2026

I have those SPP6's on all four of my SCS compressors. Helps keep from slamming the generator with a big load when the compressors kick on. I keep a couple spares as well.