(10-28-2026, 01:36 PM)Richard Wrote: I can only imagine how frustrating this is.
Let me dig around in my email files. I sent Jack a logic flow of what happens in the sequence. That logic flow may help you.
Ok, from your comments, we can deduce. The units have power, the key switches are working and have power, the pump comes on and has power.
Is it safe to assume that the coach has a box with a plexi cover that shows indicator lights? Do you have any documents that show you what those lights indicate? That is where I would start. I would also focus on ONE slideout at a time, otherwise it becomes too convoluted.
I have to ask a really stupid question. Has the fluid level been confirmed in the reservoir? Has anyone confirmed what the output pressure of the hyd pump might be?
What I don't know is if the slideouts were malfunctioning when you first touched the coach? Or they were functioning correctly and then failed. I comment because IF someone touched it before you, we DO NOT know what another person may have done, modified, or most likely connected in the wrong way. Having pulled those boxes in the tight place and fretting about connections, I can appreciate how easily a mis connection can happen. It is worse because the connectors allow this. Do you have any thoughts or insight?
Does the silver cover on the control box have a schematic pasted upon the inside?
Please don't take any questions in the wrong way. The armchair mechanics don't have the coach to view or the history to rely upon.
Jesse White recently had a front tire blowout which wreaked havoc on the HWH wiring. He had to manually (hotwire) the different solenoids to get the rooms to activate. Let's see if we can't recruit him.
Hi Richard,
Thank you for your response. I do not know what anyone else may have done to it, since it appears all the solenoids are original.
No documentation to refer to regarding lights identification in a plexi cover.
Fluid level on hydraulics reservoir is fine. Pump pressure must be OK since the slides that do work have no problems.
To my knowledge, the only thing not working was the front floor under the dinette and couch would not come up when the slide reached the full-out position. Additionally, the rear floor would not come up. However, that was repaired by complete disassembly, repair and re-assembly of the rear floor mechanism, including rebuilding the carriage system. (The hydraulic ram attachment gusset to the frame rail was literally broken off. I cut the old gusset off, strengthened the frame rail attachment, fashioned a new, more sturdy gusset and welded it to the frame rail. The rear slide floor up/down worked properly when it was put back together.)
This rear slide worked fine until we sent the board back to HWH for the second time because of the new issue involving the front slide (slide #1) continuing to EXTEND when we pushed RETRACT.
The slide #1 floor still does not come up even though I manually closed the floor-up sensor circuit when the slide reached the full out position. Like Jesse, the hot-wire master, I hot-wired the floor-up solenoid and engaged the pump from the hydraulics service bay to no avail. As I write this, it occurs to me the floor-up solenoid may be bad. (I thought I had already tested it.) Luckily, I now have 2 working spares, since I replaced 2 other solenoids thinking they may be the issue. Tomorrow, I will try replacing the floor-up solenoid and get back to you. That may be the end of the floor-up issue.
I may still have the non- RETRACT issue. This I believe, is a board malfunction.
When I refer to the lights being on or off, I am referring to the red LED indicator lights showing power to the electronics board in the hydraulics bay. There should be 5 red LEDs lit when the slides are ready to be in service (Key on, brakes set, panel keys on, yellow light on = LED light on). When we sent the board to HWH the 2nd time there was only one red LED light, of 5 lights, lit on the electronics board. When the board was returned only 4 of 5 lights on. (Almost!) The LED of the circuit panel for the non-retracting slide (Slide #1 with the non-working floor up) is not lit at all.
Inside the electronics box there are 3 circuit boards and 3 control panel boards for the slides.
In answer to your question about the schematics written on the inside panel, YES, but it is very limited. I used it to diagnose and replace several blown fuses before we sent the board back to HWH
Regarding connections being in the correct location, I painstakingly identified and labeled each connector by assigning a different color for slide 1, slide 2, slide 3, … etc, and labeled the function of each connection within the color. (6-8 functions per slide, 4 for the generator.) I used the tiny print original numbers on the wires attached to each connector to insure I had the correct wire to each connector. When I reconnected the wires, I verified the connections.
Still stumped. I imagine if I do get the slide#1 floor-up working, I may still have the non-RETRACT issue.
Once again thanks for your expertise and your input.
"In the multitude of counselors there is safety" (a good solution).
Keith