Chester,
Check the power pole where you are plugged in. Check between the two hot legs. You should show 240, but if the park cheated and wired it with only one leg you won't show any voltage from hot leg to hot leg. That would explain everything you have described.
The tricky part about diagnosing this is that all your coach meters will show 120. If you measure at the pole from hot to neutral you will get 120, only when you measure hot to hot does the problem reveal.
Check the power pole where you are plugged in. Check between the two hot legs. You should show 240, but if the park cheated and wired it with only one leg you won't show any voltage from hot leg to hot leg. That would explain everything you have described.
The tricky part about diagnosing this is that all your coach meters will show 120. If you measure at the pole from hot to neutral you will get 120, only when you measure hot to hot does the problem reveal.