This is a common issue on SQ D QO panels. Can you get a picture showing the entire panel, I bet you can get some modern guts out of a new panel and put them in the same can.
Was that the main breaker that you removed? If so that may be the problem. Now SQ D does not allow you to put branch breakers across from the main breaker like that because of this issue, overloading the bus stabs.