(07-28-2025, 01:30 PM)Richard Wrote: Keep this in mind when wiring a modified control board to the existing tstat. The outdoor fan speed is controlled by whether one or two compressors are called for. The tstat controls the indoor fan speed . So in wiring the mod board you must make provisions that the lo signal to the out door fan is interrupted when the second compressor comes on.
I accomplished this with a relay for the outdoor fan connected to the same control wire as the compressor 2 signal from the tstat. The 120v for the fan comes from the compressor 1 120v source through a normally closed contact, so that when compressor 1 comes on it also starts the fan on low speed, when the 2nd compressor kicks it changes the fan relay to change to high speed.