You are not logged in or registered. Please login or register to use the full functionality of this board...


SCS Basement AC tripping breakers
#21

Here is the report

I have 2 Scs ac units. 1 large one that uses 2 breakers, and one small one that uses 1 breaker.

The small one works fine and is pulling 15 amps at the breaker in the box.  Since this one works fine I’m going to quit talking about it.

My problem was the large one blowing breaker 1 in the breaker box after running for about 20 minutes.  This unit pulls 15 amps on breaker one and 4 amps on the second breaker in the “high fan” cool mode.  If the fan is on low it pulls no amps on breaker 2 and 15 amps on breaker 1.

Last night during the testing it worked fine.  I could not amp clamp at the ac unit itself because the wires were too short so I did all my testing at the breaker box.  I did disconnect and reconnect the compressor plugs and made sure they weren’t burnt.  It ran all night and seems to be ok so far today. 

End report

Dennis White
1997 Newell Coach 454
Canfield OH
Reply
#22

Super, thanks for taking the time to straighten out my understanding.

Two things can be discerned from your data. One, the second compressor in your large unit is NOT coming on. Two, the circuit board has some weird logic. In low cool, compressor 1, the inside and the outside fan ALL RUN off the same leg. But in high cool, compressor 1 runs and the internal fan run off leg 1, while compressor 2 and the outside fan run off leg 2. SCS did that I suppose to balance the loads as much as possible. I may have the fans reversed, but I am sure one of the fans moves to the second leg on high.

The question is to determine why comp 2 is not running.

Which breaker is tripping? 1 or 2, or both? Edit, reread your summary, breaker 1.
What size are the breakers? If 15, then we know why they are tripping Edit, I just saw the pics, they are 20 amp.


The 15 amps while running is about right given the heat we are experiencing. But you might want to continue to monitor the amp draw on that breaker as the day heats up. Higher outside temps mean higher head pressures on the compressor leading to higher amp draw

One last thing, can you remove the filters under the steps and look at the inside of the units. I know a fellow who was tripping breakers only to discover dust bunnies and a couple of coffee filters plastered on the inside evap fins.

Richard and Rhonda Entrekin
95 Newell, 390  Ex caretaker
99 Newell, 512  Ex caretaker
07 Prevost Marathon, 1025
Maverick Hybrid Toad
Inverness, FL (when we're home Cool )
Reply
#23

This pic demos what Jeff is talking about. You can see the alternating pattern where the legs would power the circuit breakers. 

https://www.google.com/search?q=picture+...AIYASACKAE

Richard and Rhonda Entrekin
95 Newell, 390  Ex caretaker
99 Newell, 512  Ex caretaker
07 Prevost Marathon, 1025
Maverick Hybrid Toad
Inverness, FL (when we're home Cool )
Reply
#24

(07-08-2026, 02:58 PM)Richard Wrote:  Super, thanks for taking the time to straighten out my understanding.

Two things can be discerned from your data. One, the second compressor in your large unit is NOT coming on. Two, the circuit board has some weird logic. In low cool, compressor 1, the inside and the outside fan ALL RUN off the same leg. But in high cool, compressor 1 runs and the internal fan run off leg 1, while compressor 2 and the outside fan run off leg 2. SCS did that I suppose to balance the loads as much as possible. I may have the fans reversed, but I am sure one of the fans moves to the second leg on high.

The question is to determine why comp 2 is not running.

Which breaker is tripping? 1 or 2, or both? Edit, reread your summary, breaker 1.
What size are the breakers? If 15, then we know why they are tripping Edit, I just saw the pics, they are 20 amp.


The 15 amps while running is about right given the heat we are experiencing. But you might want to continue to monitor the amp draw on that breaker as the day heats up. Higher outside temps mean higher head pressures on the compressor leading to higher amp draw

One last thing, can you remove the filters under the steps and look at the inside of the units. I know a fellow who was tripping breakers only to discover dust bunnies and a couple of coffee filters plastered on the inside evap fins.

So what would cause compressor 2 not to run??  Bad capacitor??  Bad compressor??  

Is the only way to access them take the entire unit out??  

I did look under the steps and there are nothing sucked against the fins

Dennis White
1997 Newell Coach 454
Canfield OH
Reply
#25

What would cause comp 2 not to run:
Signal from tstat not present on board
Power from board to comp is compromised
Compressor is burned up
Run cap is kaput

A lot of this can be tested at the circuit board without removing the whole unit.

Richard and Rhonda Entrekin
95 Newell, 390  Ex caretaker
99 Newell, 512  Ex caretaker
07 Prevost Marathon, 1025
Maverick Hybrid Toad
Inverness, FL (when we're home Cool )
Reply


Forum Jump:


Users browsing this thread: 1 Guest(s)