Generator quits
#1

Checked with Newell and was told that fuel pickup in the primary diesel fuel tank is purposely placed higher in the tank and with less than a quarter tank full may not siphon fuel adequately.  In addition if the fire extinguisher is not pressurized and in the green zone it will short the system and prevent starting the generator.  The cause of ours stopping was simply need of coolant.  Once the reservoir and overflow tank were properly filled the problem resolved.

Sandy and Bob McBratney
Previous owners of 2007 Newell #1202  "Boomer" 
Reply
#2

thanks for the reminder about the fuel pickup placement. as far as i know that is the case with all of our newells that have a single tank.

if it is warm at all, our genny is running from the time we leave till we get plugged in somewhere.

tom

2014 Haulmark 40' Super C on Freightliner Cascadia ISX15 Easton 13 speed

Former Owner 1990 38' Newell Coach 236   8V92 
Former Owner 1999 45'8" Newell Coach 526  Series 60
Former Owner 2002 45'8" Newell Coach 608 Series 60
Reply
#3

In jackflash’s post called “fuel tank leak” is a picture of the pickup tubes from my coach.  Scroll down to #8.  Pretty much the whole fuel tank replacement job is there illustrated with pictures.

Gordon Jones
1989-42~no slide-#188
2000-45'-2slide-#567
1999-45’-no slide Prevost XLV Marathon
Reply